Chances are that even if your building had a legally required (701) or optional stand by (702) system, the circuit wiring could occupy the same raceway. That is if the EM and exit fixtures have their own backup power supply. The only system that can't occupy the same raceway is emergency systems (700). Typically fixtures that have battery backup are classified as emergency systems by themselves, and fall under utilization equipment.
There are other restrictions for healthcare facilities, and separation between the Life safety, Critical care and emergency equipment.
[FONT=Arial !important]701.10 Wiring Legally Required Standby Systems.[/FONT]
[FONT=Arial !important]The legally required standby system wiring shall be permitted to occupy the same raceways, cables, boxes, and cabinets with other general wiring.[/FONT]