New area for me, as I am more of a power guy than a low voltage systems guy.
Fire alarm signals from Building #1 pass though underground ductbanks to a manhole, and from there to a central monitoring panel in Building #2. Other cables also pass through the same manhole. These include (possibly) telephone, data, and fiber optic cables. There are plans to demolish Building #2, and relocate the central monitoring panel into recently constructed Building #3. The project will also replace all the fire alarm wiring within each existing building (not the recently constructed one, though), and between each building and the central monitoring panel.
Question 1: Are there any rules within the NEC, NFPA 72, or other related codes that would require me to provide some type of separation, within the manhole, between the new fire alarm wires that I will be calling upon the contractor to install and the other miscellaneous system wires that will remain in the manhole?
Question 2: If the answer is yes, then what do you think about the suggestion that I call for the new fire alarm cables to be run within Seal-tite, as the method of providing the separation.
Fire alarm signals from Building #1 pass though underground ductbanks to a manhole, and from there to a central monitoring panel in Building #2. Other cables also pass through the same manhole. These include (possibly) telephone, data, and fiber optic cables. There are plans to demolish Building #2, and relocate the central monitoring panel into recently constructed Building #3. The project will also replace all the fire alarm wiring within each existing building (not the recently constructed one, though), and between each building and the central monitoring panel.
Question 1: Are there any rules within the NEC, NFPA 72, or other related codes that would require me to provide some type of separation, within the manhole, between the new fire alarm wires that I will be calling upon the contractor to install and the other miscellaneous system wires that will remain in the manhole?
Question 2: If the answer is yes, then what do you think about the suggestion that I call for the new fire alarm cables to be run within Seal-tite, as the method of providing the separation.