I've never done this - run a multi-wire branch circuit (12-3 UF w/ground) to a separate building. How is this done to comply with the code?
Section 250.32 exception does not require ground rods at a separate building supplied by a single or multiwire branch circuit.
OK, but then:
Section 225.31 For a separate building served by a feeder or branch circuit requires a disconnecting means. The disconnect must be suitable for use as service equipment. There is an exception for garages and outbuildings on residential property, for a snap switch.
So what it appears is for any location other than residential property, you must use a disconnect suitable for use as service equipment, which means a panel, which means its a feeder, which means ground rods.
Section 250.32 exception does not require ground rods at a separate building supplied by a single or multiwire branch circuit.
OK, but then:
Section 225.31 For a separate building served by a feeder or branch circuit requires a disconnecting means. The disconnect must be suitable for use as service equipment. There is an exception for garages and outbuildings on residential property, for a snap switch.
So what it appears is for any location other than residential property, you must use a disconnect suitable for use as service equipment, which means a panel, which means its a feeder, which means ground rods.