I am preparing to supply power to a separate building @ the manufacturing plant were I work. One general lighting circuit and one heating circuit.The separate building is metal framed and is utilized as a smoking area for employees.
Feed is a 4 wire(2 phase conductors,1 grounded conductor/neutral,and 1 equipment grounding conductor), 50A 240v 1ph circuit breaker, from a remote location inside the existing building, supplying a outdoor sub-panel w/ (1) 20A 120V GFCI & (1) 30A 240V GFCI circuit breaker (used as disconnects for separate building), which will be mounted on the outside wall of the existing building. The separate building is 6ft. away from the outside wall(sub-panel) and I am using direct burial cable to supply the fixtures & equipment in the separate building. I will use ground rods to establish ground at the sub-panel and terminate Grounding Electrode Conductor and Equipment Grounding Conductors @ the sub-panel and maintain separation of grounded conductor/neutral. I will bond conduit (housing cable to required burial depth) @ sub panel to the established ground @ sub panel, & bond incoming conduit @ separate building.
Questions:
1. Should I install an additional ground rod(separate of the grounding electrode @ sub-panel) and bond the metal frame of the building through the grounding electrode conductor, since there is no metal path way between the sub-panel and the separate building?
2. Is there anything that I have overlooked or misinterpreted concerning this installation?
Feed is a 4 wire(2 phase conductors,1 grounded conductor/neutral,and 1 equipment grounding conductor), 50A 240v 1ph circuit breaker, from a remote location inside the existing building, supplying a outdoor sub-panel w/ (1) 20A 120V GFCI & (1) 30A 240V GFCI circuit breaker (used as disconnects for separate building), which will be mounted on the outside wall of the existing building. The separate building is 6ft. away from the outside wall(sub-panel) and I am using direct burial cable to supply the fixtures & equipment in the separate building. I will use ground rods to establish ground at the sub-panel and terminate Grounding Electrode Conductor and Equipment Grounding Conductors @ the sub-panel and maintain separation of grounded conductor/neutral. I will bond conduit (housing cable to required burial depth) @ sub panel to the established ground @ sub panel, & bond incoming conduit @ separate building.
Questions:
1. Should I install an additional ground rod(separate of the grounding electrode @ sub-panel) and bond the metal frame of the building through the grounding electrode conductor, since there is no metal path way between the sub-panel and the separate building?
2. Is there anything that I have overlooked or misinterpreted concerning this installation?