If you had 5-6 20 receptacles in a wall next to each other( about 3' apart) that utilized EMT how would they be wired? I am assuming becuase they are seperate ckts. you could not just run emt recept to recept and splice thought. Too many wires in a box and it would be tight. Would you have to run a separate conduit up the wall to a box for each. Thanks.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
For the most part, I prefer receptacle wiring to be run above the drop ceiling level to j-boxes, and from there down to receptacles. It makes it easier to make changes later on, without having to tear into walls. But I don't object to using flex from receptacle to receptacle within the same wall, and have approved requests from ECs to allow that change.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the boxes are large enough and the condcutors are properly derated you can run box to box. Two conduits with 3 boxes each might be a better setup.
 

renosteinke

Senior Member
Location
NE Arkansas
It's a good design and trade practice issue, and not limited to just above dropped ceiling.

Let's begin with the obvious: There's no law that says all the wires have to pass through every box, and boxes come in many sizes. There's also a role for more than one type of wire connector.

In a typical such situation, I tend to have my 'home runs' go to a large, deep metal box. Either the box is in some place like an attic, with a blank plate cover .... or it's behind the first device. Deep? I might even use an extension ring for more depth or more connection points.

Then there's the fine point of ID of your neutral wires. While not strictly necessary, I find it reassuring to be able to confirm that I'm using the 'right' neutral. I usually mark them with a single colored stripe, using a Sharpie.

It's really nice if you can run the un-used (at that point) wires straight through the boxes. Failing that, it's time for something besides wire nuts.

"Ordinary" Wagos, or the Ideal In-sure connectors, are permanent; you can't remove the wires without damaging things. I use these where I want to make it difficult to open up the connection.

Where a device pigtail attaches, or I can forsee any circumstance that requires the wires to separate, I like the Wagos with the tiny levers. These let you remove individual wires without disturbing the other connections. I especially like this for neutrals on multi-wire circuits.

The final detail is the use of wire numbers, as well as colors, to identify things.

If you're using MC as your method, use the blue circuit for the devices closest to the panel. Then you can 'downsize' to red, and finally only black, as you move along - not having to reidentify anything.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
It's a good design and trade practice issue, and not limited to just above dropped ceiling.

Let's begin with the obvious: There's no law that says all the wires have to pass through every box, and boxes come in many sizes. There's also a role for more than one type of wire connector.

In a typical such situation, I tend to have my 'home runs' go to a large, deep metal box. Either the box is in some place like an attic, with a blank plate cover .... or it's behind the first device. Deep? I might even use an extension ring for more depth or more connection points.

Then there's the fine point of ID of your neutral wires. While not strictly necessary, I find it reassuring to be able to confirm that I'm using the 'right' neutral. I usually mark them with a single colored stripe, using a Sharpie.

It's really nice if you can run the un-used (at that point) wires straight through the boxes. Failing that, it's time for something besides wire nuts.

"Ordinary" Wagos, or the Ideal In-sure connectors, are permanent; you can't remove the wires without damaging things. I use these where I want to make it difficult to open up the connection.

Where a device pigtail attaches, or I can forsee any circumstance that requires the wires to separate, I like the Wagos with the tiny levers. These let you remove individual wires without disturbing the other connections. I especially like this for neutrals on multi-wire circuits.

The final detail is the use of wire numbers, as well as colors, to identify things.

If you're using MC as your method, use the blue circuit for the devices closest to the panel. Then you can 'downsize' to red, and finally only black, as you move along - not having to reidentify anything.