Skyline Electrical
Member
- Location
- wa
- Occupation
- electrician
I've got a client that has two 1in pvc runs from a crawlspace to a carport under a poured driveway. My current wire fill calc is not up to snuff with the feed and comm conductors I need to run, if I only consider 1 of the conduits.
Can I split the L1 and L2 feeds in a pvc box on one end, run each leg in its own PVC with N and G, and combine again on the far side of the run in another pvc box? I've found some guidance on more industrial/commercial splitting of phases in this manner and mostly just to ensure that there is no metal rings in the run for inductance. I'm looking at 300.3b3
The 2 conduits share the same 'trench' and the entire installation would be nonferrous
Am I correct in this interpretation?
Can I split the L1 and L2 feeds in a pvc box on one end, run each leg in its own PVC with N and G, and combine again on the far side of the run in another pvc box? I've found some guidance on more industrial/commercial splitting of phases in this manner and mostly just to ensure that there is no metal rings in the run for inductance. I'm looking at 300.3b3
The 2 conduits share the same 'trench' and the entire installation would be nonferrous
Am I correct in this interpretation?