Hello,
Working on a remodle of a fire station in WI. Mostly HVAC upgrades: New Boiler, AHU, etc. Some small archy wall changes.
I was at the site the other day and it appears as if the emergency generator is backing up the entire building.
Service conductors come in and hit a 400a disc. then go thru a CT cab. w/ meter and hit a wire way. In this wireway the these conductors are spliced with a panelboard feed, a motor feed, and a set of conductors to a 200a ATS. ATS then feeds panel MDP (main distribution panel - MLO - 400a). ATS is also feed via generator 50 KW - 120/208 - Nameplate rating of 174a.
...So normal is lost on the and the ATS will switch to the gen backing up all of MDP.
We are doing some lighting upgrades in some rooms and a corridor or two....but I only have one ATS and loads are not seperated from life safety to Equipment (the whole building is backed up). I think there is 6 branch panelboards in the whole building and every one has at least 1 exit light circuit, etc.
At what point am I required to updated all this....? It is all from the early 60's, they don't have a ton of money and want to spend it on HVAC upgrades.
Thoughts?
Working on a remodle of a fire station in WI. Mostly HVAC upgrades: New Boiler, AHU, etc. Some small archy wall changes.
I was at the site the other day and it appears as if the emergency generator is backing up the entire building.
Service conductors come in and hit a 400a disc. then go thru a CT cab. w/ meter and hit a wire way. In this wireway the these conductors are spliced with a panelboard feed, a motor feed, and a set of conductors to a 200a ATS. ATS then feeds panel MDP (main distribution panel - MLO - 400a). ATS is also feed via generator 50 KW - 120/208 - Nameplate rating of 174a.
...So normal is lost on the and the ATS will switch to the gen backing up all of MDP.
We are doing some lighting upgrades in some rooms and a corridor or two....but I only have one ATS and loads are not seperated from life safety to Equipment (the whole building is backed up). I think there is 6 branch panelboards in the whole building and every one has at least 1 exit light circuit, etc.
At what point am I required to updated all this....? It is all from the early 60's, they don't have a ton of money and want to spend it on HVAC upgrades.
Thoughts?