We have been doing this for years but now an inspector that we do not know turned us down for this.
When an electric furnace requires (3) 60 amp 240v circuits and (1) 30 amp 240v circuit, we would mount a 100 amp MLO panel next to the furnace and feed it from the main panel with 100 amp SEC....just 2 hots and a ground, no neutral since this panel is for 240v equipment only and simply acting as disconnects for the equipment ( furnace ).
The inspector says this needs to be treated like a subpanel and needs a neutral ran to it as well which needs to be isolated from equipment ground.
Where in the NEC can I find this particular installation? I can't find it in feeders or sevice disconnects. ANY HELP WILL BE GREATLY APPRECIATED!:-?
When an electric furnace requires (3) 60 amp 240v circuits and (1) 30 amp 240v circuit, we would mount a 100 amp MLO panel next to the furnace and feed it from the main panel with 100 amp SEC....just 2 hots and a ground, no neutral since this panel is for 240v equipment only and simply acting as disconnects for the equipment ( furnace ).