RobertRheintgen
Member
- Location
- Westmont, IL
We were installing a generator and showed the letter from Bob Cramer from Generac. The inspector is citing section 250.20 of the NEC and 250.20(D) He is saying if the transfer switch does not transfer the neutral (grounded conductor), then the generator has a "solidly connected" grounded circuit conductor and the generator is not a separately derived system. Is there any documentation we can provide to this inspector beyond the Generac letter that may help our situation. He wants a ground rod. Thank you!