I have a question about transfer of neutral in the transfer switch.
I had another electrician tell me about a recent install his company had done.
A 480 volt 75 Kva generator was relocated from a building to a new location. At the new location the service provided by utility is 120 / 208 volt. They installed the 480 volt generator and fed a step down transformer 120 / 208 volt secondary. From the transformer they installed a piece of greenfield they installed 3 hots, neutral and a equipment grounding conductor to a 3 pole transfer switch. The neutral and grounds are isolated in the transfer switch. The other side of the transfer switch is fed from a feeder with 3 hots, neutral, and equipment grounds. They have the feeder neutral and the secondary transformer neutral connected together in the transfer switch. The equipment grounds from transformer and feeder are connected together in transfer switch. I told them that because of the transformer being installed that it is a seperately derived system and that the neutrals should be switched because of parallel path in the equipment grounding conductors and the neutrals because back at the service equipment they are tied together. To top it off this is feeding I.T. equipment. What do you guys say?