Re: Seperately Derived System
Q1.Does the GEC need to all the way back to the building ground or does it just get bonded at the service or building steel?
A1. The requirements for GEC SDS systems are covered by 250.30(4). Basically the nearest practical location in the order of:
1. Effectively grounded structure metal member of the structure (building steel).
2. Water pipe within 5 feet of building entrance.
3. Other electrodes specified by 250.52.
The code gives the minimum requirements, but there are some performance methods used in data centers like using the signal reference grid under the raised floor, or rebar stubbed up for the purpose.
Q2. Also, what is the purpose of the extra ground wire (GEC)? Is this just a backup to the grounding conductor?
A2. Good question and you will get different answers. IMO it has to do with current transfer ratio of the transformer, and the distance of the primary input EGC. For example with a step down transformer, the output current is higher than the input, therefore the primary EGC would not be thermally capable of clearing a secondary fault to local building steel. Couple that with the distance and the added impedance, the impedance may not be low enough to operate the secondary OCPD.
Then there are some technical performance issues with respect to high frequency common mode noise involved with long EGC circuits. But I will not open that can of worms now. Hope that helps.