I have typical 225KVA 480/120/208 transformer serving a fusible disconnect on its secondary, ultimately feeding a few 208/120V panel boards.
I have bonded the neutral XO tap in the transformer to the grounding lug within, along with my GEC to building Steel.
Question: the disconnect is my 1st means of disconnect. Do I need to re-bond the neutral in the disconnect to the grounding buss or shall I float the neutral?
Thanks in Advance
I have bonded the neutral XO tap in the transformer to the grounding lug within, along with my GEC to building Steel.