Septic system requirements

Status
Not open for further replies.

crtemp

Senior Member
Location
Wa state
I have always installed a separate 15 amp circuit for the controls and alarm and a separate 20 amp circuit for the pump. My question is, is it code to install the dedicated circuit for the controls or could this just be tapped off of any lighting circuit? I can’t seem to find anything in the NEC or in the manufacturers instruction one way or another.
 
I always put the alarm on a different (mostly a newly run) circuit than the pump. If the pump trips the circuit and the alarm is on the same circuit, the alarm won't activate.
 
Aside from circuit dedication would be tank wiring configuration.

Some localities require the disco by the tank, parsing code to pass...

Most have a breather tube that one can park a 6x6PT by

As the tank is a methane atmosphere, it's best not to assume any splicing(s) within it, as well as all diagnostics (south of a stuck float) external of it

So we do a 2" pvc out of the tank, to the 6x6 post , all cords are run through, sealed w/ dux

Not the 'pristine' install, but less resi woes ...what say the crew?

~RJ~
 
Check the rules for whatever agency has jurisdiction over the septic installs. In TN the alarm is required to be on a separate circuit.
 
Check the rules for whatever agency has jurisdiction over the septic installs. In TN the alarm is required to be on a separate circuit.

Thats a good point. I think in certain county’s here in Washington I’m even required to install a knife switch disconnect where as other places just a 60 amp pullout disco is fine. I never really understood why I needed a disconnect before the control box when it has breakers inside it that kill all power to the control box and tank. Maybe it’s a building code. I’ll see if I can find anything on the county website. Mainly I only do these installs in Clark and cowlizt county.
 
Thats a good point. I think in certain county’s here in Washington I’m even required to install a knife switch disconnect where as other places just a 60 amp pullout disco is fine. I never really understood why I needed a disconnect before the control box when it has breakers inside it that kill all power to the control box and tank. Maybe it’s a building code. I’ll see if I can find anything on the county website. Mainly I only do these installs in Clark and cowlizt county.
Someone that will profit more was involved in making the rules??
 
At my house, the alarm is on its own circuit. Today, I would prefer to put it on one of the lighting circuits, so if it somehow got turned off or tripped, I would know it.
 
At my house, the alarm is on its own circuit. Today, I would prefer to put it on one of the lighting circuits, so if it somehow got turned off or tripped, I would know it.

That is also why you shouldn't put smoke alarms on a dedicated circuit, although it's permitted (NFPA 72-2010 29.6.3(5)).
 
Aside from circuit dedication would be tank wiring configuration.

Some localities require the disco by the tank, parsing code to pass...

Most have a breather tube that one can park a 6x6PT by

As the tank is a methane atmosphere, it's best not to assume any splicing(s) within it, as well as all diagnostics (south of a stuck float) external of it

So we do a 2" pvc out of the tank, to the 6x6 post , all cords are run through, sealed w/ dux

Not the 'pristine' install, but less resi woes ...what say the crew?

~RJ~

Sounds like an outdated way of doing things. All the Orenco Systems I have done in the past 3 months (4 and counting) have external j-boxes factory mounted to the tank. All you do is pipe it, bring the float and pump cords into the cord grips, and terminate.
 
Though sort of wise to put alarm on separate circuit - still good idea to get alarm with a battery backup.
 
Thats a good point. I think in certain county’s here in Washington I’m even required to install a knife switch disconnect where as other places just a 60 amp pullout disco is fine. I never really understood why I needed a disconnect before the control box when it has breakers inside it that kill all power to the control box and tank. Maybe it’s a building code. I’ll see if I can find anything on the county website. Mainly I only do these installs in Clark and cowlizt county.

This was explained in an Electrical Currents article some years ago, I tossed all my printed copies, but they are available on line.
 