• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Sequences

Merry Christmas

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
I am reading a paper about short circuit current calculations; the author speaks of positive, negative, and zero sequences but doesn't define them. I have heard the terms before but I never truly understood them; can someone enlighten me as to what they mean? I would appreciate it. I can see that they have something to do with AC impedances.

Mods: please remove the duplicate from the General Electrical forum.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Larry is correct, sequences are part of symmetrical components. Kind of hard core engineering.

These are very helpful when analyzing unbalanced 3-phase circuits. We can use the negative sequence to look at if a utility fuse has blown causing our transformer to develope a phantom voltage thus fooling phase loss relays. Zero sequence currents are used with GF systems and 'artificial neutral and grounding' transformers.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
And then there's this kind:

1716871480046.jpeg
biggrin.gif
 