SER Aluminum amperage 75 amps ?

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
I only see USE in the ampacity table. Is SER rated the same ampacity rating as USE ? Mnf says I have to install a 70 amp sub panel for 2 infratech heaters rated 25 amps each. NEC has #4 USE aluminum for 75 amps. Is SER the same rating? I realize it will not be used for service entrance, that makes it rate less? Is the NEC #4 rated for 75 amps only if used for service entrance? Thank you!
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Aluminum SE cable has Type XHHW-2 or Type THHN/THWN-2-insulation.

Construction​



"Southwire Type SE cable is constructed with Alumaflex® AA-8000 series aluminum alloy, compacted stranded conductors. The conductors are covered with a sunlight resistant Type XHHW-2 or Type THHN/THWN-2-insulation. A reinforcement tape is wrapped around the conductors for added strength and conformity. A gray sunlight-resistant polyvinyl chloride (PVC) outer jacket covers the entire assembly. Style SEU cable has two phase conductors surrounded by a concentric neutral while the SER style has two, three or four phase conductors and a bare neutral. Southwire Style SER Cable’s phase conductors are identified by a colored stripe on the insulation:
 

Eddie702

Licensed Electrician
Location
Western Massachusetts
Occupation
Electrician
For a service entrance the cable or conductors need only be rated at 83% of the main breaker so #$ copper or #2 alum for a 100 amp service and 2/0 copper and 4/0 aluminum for a 200 amp service.

This has nothing to do with normal wiring which you use the standard ampacity tables for and derate for temperature and # of conductors if need be.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This has nothing to do with normal wiring which you use the standard ampacity tables for and derate for temperature and # of conductors if need be.
Since he's asking about wiring a feeder to a sub-panel this would fall under the normal wiring you've mentioned.
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
You are limited to the 75C column even if the wire insulation has 90C insulation due to the 75C max terminations of the equipment.

I have never seen any sizing recommendations of "sub panel" from Infratech. They will specify the feeder size when they are supplying a control panel. Their control panels have individual breakers for each heater. The size of the feeder will be the total load of the heaters * 125%.
(2) 6,000 water heaters would work out to a 62.5 amp feeder, so 70 amps is the next standard size.
 

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
You are limited to the 75C column even if the wire insulation has 90C insulation due to the 75C max terminations of the equipment.

I have never seen any sizing recommendations of "sub panel" from Infratech. They will specify the feeder size when they are supplying a control panel. Their control panels have individual breakers for each heater. The size of the feeder will be the total load of the heaters * 125%.
(2) 6,000 water heaters would work out to a 62.5 amp feeder, so 70 amps is the next standard size.
Yes, you are correct, a control panel. But since they said it will have two 30 amp breakers, I thought I should treat it like a sub panel and use a 4 wire feeder. They actually told me to use a 3 wire.
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Yes, you are correct, a control panel. But since they said it will have two 30 amp breakers, I thought I should treat it like a sub panel and use a 4 wire feeder. They actually told me to use a 3 wire.
Subpanel is just trade slang. It has no technical meaning.

The single phase heater control panels require 3 wires L1/L2/EGC. No neutral required.
 