I'm looking to the forum collective wisdom on this:
What is the rating of 4-4-4-6 SER Aluminum for feeding a sub-panel? 75 degree rating is 65amps, next breaker size up is 70 amps
What's the rating of 1/0-1/0-1/0-2 SER Aluminum for feeding a sub-panel? 75 degree rating 120amps, next breaker size is 125 amps.
This is based on the breakers and panels being rated for 75 degrees
Is this your understanding? Please correct me if I'm wrong.
Thanks folks