we have some 2/4 SER cable thats marked XHHW insulation on the outer covering. is this used as a 60 degree cable or 75?
we have some 2/4 SER cable thats marked XHHW insulation on the outer covering. is this used as a 60 degree cable or 75?
XHH --Indicates a single conductor having a cross-linked synthetic polymer insulation with no overall covering provided, rated 90?C dry.
XHHW -- Indicates a single conductor with the same description as Type XHH, except that it is rated 90?C dry, 75?C wet.
UL White Book ZKST:
But he is not using a single conductor..
~Matt
I don't use single conductors when I install NM, either.
we have some 2/4 SER cable thats marked XHHW insulation on the outer covering. is this used as a 60 degree cable or 75?
depending on the code cycle - nm is 60 degree though.
~Matt
we have some 2/4 SER cable thats marked XHHW insulation on the outer covering. is this used as a 60 degree cable or 75?
Check to see if the conductors are -2 type that allows 90C rate for both WET or Dry.
There are almost no instances where we can use the 90 C rating of SE regardless of it being XHHW-2 or not.
With the changes in the 2008 NEC SE used as indoor feeder or branch circuit conductors is limited to the 60 C rating.
Used as service entrance conductors we are limited to 75 C rating due to the rating of the devices it will connect to.
you keep referencing nm does the 60 degree also apply to rx when ampacity is involved?