brichter
Member
- Location
- Northern Indiana
Is it code compliant to install aluminum SER in ridgid non-metallic conduit underground?
See this thread for the recent argument on the matter.brichter said:Is it code compliant to install aluminum SER in ridgid non-metallic conduit underground?
I would have to disagree with that. A conduit's interior is not a location, whether above or underground. Any conductor or cable installed underground, whether in a conduit or not, must be rated for wet locations.georgestolz said:In my opinion, SE cable installed inside a conduit is not underground.
LarryFine said:Direct-burial is a separate listing, and is required for any cable or conduit underground and not in a conduit. There is a difference between underground and direct-burial as far as the NEC is concerned.
LarryFine said:A conduit's interior is not a location, whether above or underground. Any conductor or cable installed underground, whether in a conduit or not, must be rated for wet locations..
iwire said:If the conduit is not a 'location' than we would need to install conductors in that conduit that are rated for underground use, not simply type 'W" conductors.
On the one hand your saying SER (which is rated for wet locations) can not be installed in a conduit underground.
On the other hand your saying that THWN which is only rated wet can be installed in a conduit underground.
You can not have it both ways.![]()
The companion thread to this one, linked to in the thread, can't be reached through the links in the thread, due to the recent forum change.georgestolz said:See this thread for the recent argument on the matter.
The cable is not underground, but that doesn't remove it from the ire of 300.5:LarryFine said:No, I was responding to George's "In my opinion, SE cable installed inside a conduit is not underground." This is similar to the discussion about using NM in conduit outdoors. If the conduit is outdoors, so is the wiring inside.
IMO, the way this is worded you could call the inside of the pipe vegetable soup, and it wouldn't matter. It's a cable inside a raceway underground, so it must be listed for wet locations. It never outright calls the inside of the pipe underground, or even wet for that matter.(B) Listing. Cables and insulated conductors installed in enclosures or raceways in underground installations shall be listed for use in wet locations.
It is if it's inside a conduit that is underground. The original post asked:georgestolz said:The cable is not underground . . .
brichter said:Is it code compliant to install aluminum SER in ridgid non-metallic conduit underground?
Absolutely.georgestolz said:It's a cable inside a raceway underground, so it must be listed for wet locations.
It doesn't have to; if it's underground, it's underground, and it's a wet location, conduit or no. Above ground outdoors and unprotected by cover is also a wet location, conduit or no.It never outright calls the inside of the pipe underground, or even wet for that matter.![]()
georgestolz said:I would think the UL might be a better source. The NFPA might just regurgitate the text of 300.5, and follow it up by a 110.3(B), which leaves us back where we were.![]()
georgestolz said:I would think the UL might be a better source. The NFPA might just regurgitate the text of 300.5, and follow it up by a 110.3(B), which leaves us back where we were.![]()
And I thought we had it all resolved in those other threads.