chevyx92
Senior Member
- Location
- VA BCH, VA
Under the 2005 NEC what column do you size under, 60 degree or is it the 75? I heard this had changed, when??
2005 you use 75C and 2008 you use 60C. For derating you may use 90C for both.chevyx92 said:Under the 2005 NEC what column do you size under, 60 degree or is it the 75? I heard this had changed, when??
Dennis Alwon said:2005 you use 75C and 2008 you use 60C.
.
Under the 2008 as well or just 2005?Dennis Alwon said:Remember if it is for Service and not a feeder then the 75C still is applicable.
chevyx92 said:Under the 2008 as well or just 2005?
mark32 said:Which article contains this change, I can't find it.
mark32 said:Thank you RUWired. Just so I am on the same page as everyone else lets look at a common scenario. Someone runs #2 aluminum SER to feed a sub panel and even though the terminations are rated 60/75c the SER's OCPD must be sized to the 60c column(?) this case being an 80 amp breaker sized up one size from 75. Is this correct?
mark32 said:Strange indeed Stickboy. I work at HD and guys come in and buy #2 al SER all the time and most want to put it on a 100a breaker. I would tell them it's only rated for a 90 but now it's dropping down to a 70! (Suppose I'd rather do that than up sizing to an 80 as you pointed out)
RUWired said:One exception that would allow the # 2 awg sub panel feed is, if the service conductors are #2 awg al for a 100 amp service, # 2awg for a sub panel would be allow.
215.2 Minimum Rating and Size.
(A) Feeders Not More Than 600 Volts.
(3) Individual Dwelling Unit or Mobile Home Conductors. Feeder conductors for individual dwelling units or mobile homes need not be larger than service conductors. Paragraph 310.15(B)(6) shall be permitted to be used for conductor size.
frankft2000 said:Another exception is table 310.15(B)(6) conductor types and sizes for 120/240 volt, 3 wire, single phase dwelling services and feeders. 100 amps, use #4 copper or #2 aluminum
frankft2000 said:Another exception is table 310.15(B)(6) conductor types and sizes for 120/240 volt, 3 wire, single phase dwelling services and feeders. 100 amps, use #4 copper or #2 aluminum
mark32 said:I just looked over my '05 codebook and the NM section pertaining to ampacity (334.80) is, if I'm not mistaken, unchanged to the '08 code. Am I missing something?
Dennis Alwon said:This is only true if the feeder is on the exterior of the building. Interior wiring with seu or ser as feeders must use the 60C rating.
infinity said:Where do you find the interior/exterior delineation in the code book? As Hillbilly said if the feeder supplies 100% of the load Table 310.15(B)(6) may be used regardless of where that feeder is installed.
Dennis Alwon said:How do you interpret 338.10(B)(4)(a)
infinity said:IMO that doesn't apply to feeders that fall under 310.15(B)(6) if the service entrance conductors and the feeder are the same size.