Am I correct that it is generally no longer possible to run a Aluminum 200A SER cable for a feeder that does not serve an entire dwelling and would be required to run through some insulation in an attic?
The Scenario:
I have a 200A meter/main service disconnect that also has room for 8 breakers that will be installed on the exterior of a dwelling.
It has feed thru lugs for a indoor 200A panel. That loadcenter is called out a ways inside the dwelling.
Since some outdoor loads and the range will be landed in the outdoor meter/main the "entire" dwelling will not be supplied from the feeder.
338.10(B) States we must use 60C column for ampacity if contact with insulation.
Now the cable is going in an attic space and could possibly be run above the insulation.
Assume the AHJ will interpret it as in contact with insulation for this discussion.
SER is not made over 250kcmil
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet273
310.15(B)(16) lists 250kcmil AL at 170A under 60C
240.6 States 175 is a standard size breaker.
So we would need a 300kcmil SER cable to use the feed through lugs protected by the 200A main.
So if you want to run a 200A feeder in thermal insulation it has to be in conduit of some type.
Just need to think this through
Thoughts?
The Scenario:
I have a 200A meter/main service disconnect that also has room for 8 breakers that will be installed on the exterior of a dwelling.
It has feed thru lugs for a indoor 200A panel. That loadcenter is called out a ways inside the dwelling.
Since some outdoor loads and the range will be landed in the outdoor meter/main the "entire" dwelling will not be supplied from the feeder.
338.10(B) States we must use 60C column for ampacity if contact with insulation.
Now the cable is going in an attic space and could possibly be run above the insulation.
Assume the AHJ will interpret it as in contact with insulation for this discussion.
SER is not made over 250kcmil
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet273
310.15(B)(16) lists 250kcmil AL at 170A under 60C
240.6 States 175 is a standard size breaker.
So we would need a 300kcmil SER cable to use the feed through lugs protected by the 200A main.
So if you want to run a 200A feeder in thermal insulation it has to be in conduit of some type.
Just need to think this through
Thoughts?