To add to what Bryan has posted, also talk the the AHJ, as I have read on the posts here that there are some jurisdictions that do not permit NM type cables in commercial installations.
338.10(B)(4)(a) sends you to Parts I & II of Article 334 which sets out uses permitted at 334.10 (1)(2)&(3). If you read closely enough, you'll see that SER would not be allowed exposed in dropped or suspended ceilings in your subject commercial building. It would be required to have a 15 minute finish rating as identified in listing of fire-rated assemblies.
Also, as has been pointed out, there may be a local law prohibiting the use of NM cable as well.
Check with the local AHJ. :smile: