(C) In Unfinished Basements and Crawl Spaces. Where
cable is run at angles with joists in unfinished basements
and crawl spaces, it shall be permissible to secure cables
not smaller than two 6 AWG or three 8 AWG conductors
directly to the lower edges of the joists. Smaller cables
shall be run either through bored holes in joists or on running
boards. Nonmetallic-sheathed cable installed on the
wall of an unfinished basement shall be permitted to be
installed in a listed conduit or tubing or shall be protected
in accordance with 300.4. Conduit or tubing shall be provided
with a suitable insulating bushing or adapter at the
point the cable enters the raceway. The sheath of the
nonmetallic-sheathed cable shall extend through the conduit
or tubing and into the outlet or device box not less than
6 mm (1⁄4 in.). The cable shall be secured within 300 mm
(12 in.) of the point where the cable enters the conduit or
tubing. Metal conduit, tubing, and metal outlet boxes shall
be connected to an equipment grounding conductor complying
with the provisions of 250.86 and 250.148.
Yes. If not fused that's a problem.If that SE connector on the right is going into the back of the meter around here you would have a problem with the length of the SEC's inside of the structure.
That is ser cable so I assume there is a main panel outside,
Good point but I do see two bare conductors that appear to be GEC's.
Yes. If not fused that's a problem.
Just frame in some sheeting in the stud bays where the wire is exposed so it isn't accessible anymore and not subject to physical damage. No reason to redo it in conduit.
I agree. And shouldn't those walls have some kind of fire rated covering on them anyway?
Except for the common wall between garage and habitable space.Not in an unfinished garage....
Except for the common wall between garage and habitable space.
Good point but I do see two bare conductors that appear to be GEC's.
I see the same thing and share the same opinion.That looks like it could be 4 conductor cable, so there may be other problems as well if there is a breaker outside and the bond is outside and the GEC's are out of that panel.....
WJust to clarify. The ser is going from a main panel to a sub. The sub is in the garage.
Sent from my iPhone using Tapatalk
But this is within a garage and has nothing to do with an unfinished basement or crawl space as referenced in your post. (probably just for clarification i'm sure)Se cable would follow the same rule in this matter as nm cable