Can i run ser in conduit. what sheathed 100 or 200 amp cable al or cu can j not run in conduit ???????????????????
That last part is state specific for short sections but NEC yes you're correct.You can run any cable in conduit, with exceptions. SER can't be ran underground, in, or out, of conduit.
NM cable can't be outside, in or out of conduit
Exceptions to SER in conduit being temporary underground installations?You can run any cable in conduit, with exceptions. SER can't be ran underground, in, or out, of conduit.
NM cable can't be outside, in or out of conduit
Yes, but there are lots of things allowed in temp installations that aren't allowed in general wiring. I was speaking of general wiring as I supposed the OP was asking about.Exceptions to SER in conduit being temporary underground installations?
590.4(B)(2)
590.4(C)(2)