You can run any cable in conduit, with exceptions. SER can't be ran underground, in, or out, of conduit.
NM cable can't be outside, in or out of conduit
Exceptions to SER in conduit being temporary underground installations?

590.4(B)(2)
590.4(C)(2)
 
In my area the inspectors wanted SER coming out of outdoor service circuit breaker to be in conduit from the top of the panel to at least 8' above the ground to protect the cable. Same with SER cable leaving the bottom of a panel.
 