HoosierSparky
Senior Plans Examiner, MEP
- Location
- Scottsdale AZ
- Occupation
- Senior Plans Examiner
I have a contractor that installed SE cable, exposed, in the ceiling of a garage. Oops! That isn't what was shown on the plans. Double Oops! The cable is not supported correctly either and has been cited for that too (Article 338). He is proposing to cover the supported cable with a sheet metal enclosure. The "shots" and/ or threaded rod is not embedded enough or properly. I believe the enclose constitutes a raceway and should be bonded. Any other observations? Comments? Thanks.