I know you can't use SER cable in underground conduit, but can you use it above ground in conduit outdoors?
If no, why can it be ran outdoors exposed and why does it say sunlight resistant on the sheathing?
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Sure you can.
Not sure why some think you can’t…
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It is the ug that is the issue. Very unlikely for water to sit in a conduit above grade but it really should be installed to drain anyway.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
I think they are thinking it is like NM cable which can't be outside, conduit or not.
I’ve had people tell me UF can’t be in pipe.

NC has an exclusion for NM outside for something like an AC feed in a piece of carflex.
 

Buck Parrish

Senior Member
Location
NC & IN
I saw this install near ISU. The SER goes up two floors. I've always put mine in conduit. But could be a lot of profit to be made doing services like this.
20170418_093813 (3).jpg
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I have seen that also and it is legal. If you tell the young guys around here that it is complaint they raise an eyebrow because it just isn't done here. In fact, even on temp poles we use pvc.

Those cables aren't strapped within a foot of the box and IMO, it is subject to damage. The way it enters the building is questionable
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
I think underground wet is more corrosive to aluminum wire than above ground wet. Not all SER is aluminum, but much of it is. And that aluminum grounding conductor is usually bare underneath the sheath. One little hole in the sheath and it gets water in it.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
I don’t know why that isn’t “subject to damage”
Because it's installed in a part of the country where the convention is not to go around attacking cables on the sides of buildings? As opposed to other parts of the country, where people worry that may happen.

Cheers, Wayne
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
TN Code supplemented the NEC:
0780-02-01-.10 SERVICE ENTRANCE CONDUCTORS. Service entrance conductors shall be installed
in conduit where such conductors serve a structure with exterior walls of brick, stone, masonry, metal or
metal-clad.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Because it's installed in a part of the country where the convention is not to go around attacking cables on the sides of buildings? As opposed to other parts of the country, where people worry that may happen.

Cheers, Wayne
Looking at the pic it looks like the cable is laying against the corner of the cabinet. SER won’t hold that curve without laying against something or strapped real tight.
also, as Dennis pointed out, it isn’t strapped correctly.
But I guess someone could attack the cable if they were so inclined...
I‘ve installed SER going in just like that one at the bottom.
Inspector required a strap..
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Looking at the pic it looks like the cable is laying against the corner of the cabinet. SER won’t hold that curve without laying against something or strapped real tight.
Hard to tell because of the camera angle, and there are strap above and below that offset.

Otherwise, I agree with what you said, but my comments were limited to the question you raised about "subject to damage."