A Alwayslearningelec Senior Member Location NJ Occupation Estimator Nov 8, 2022 #1 When using SER cable for temporary situation can one use the 90 degree column ampacity rating or still need to make sure terminals on equipment are rated 90 degree?
When using SER cable for temporary situation can one use the 90 degree column ampacity rating or still need to make sure terminals on equipment are rated 90 degree?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Nov 8, 2022 #2 In general there is no 90° C rated equipment that you would use SE cable with so you're stuck at 75° C ampacity with 75° C terminals.