SER Cable Temp Rating

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
When using SER cable for temporary situation can one use the 90 degree column ampacity rating or still need to make sure terminals on equipment are rated 90 degree?
 
In general there is no 90° C rated equipment that you would use SE cable with so you're stuck at 75° C ampacity with 75° C terminals.
 