Have I ever seen an inspector allow it (buried) on a temp service? YesType SE. Service-entrance cable having a flame-retardant, moisture-resistant covering.
Type USE. Service-entrance cable, identified for underground use, having a moisture-resistant covering, but not required to have a flame-retardant covering
Type SE ? Indicates cable for aboveground installation. Both the individual insulated conductors and the outer jacket or finish of Type SE are suitable for use where exposed to sun.
Types USE and USE-2 ? Indicates cable for underground installation including direct burial in the earth. Cable in sizes 4/0 AWG and smaller and having all conductors insulated is suitable for all of the underground uses for which Type UF cable is permitted by the NEC. Types USE and USE-2 are not suitable for use in premises or aboveground except to terminate at the service equipment or metering equipment. Both the insulation and the outer covering, when used, on single and multiconductor Types USE and USE-2, are suitable for use where exposed to sun.
No, SEU is in the "SE" category. It's not suitable for direct burial.Originally posted by macmikeman:
Well we got type ser and use, but does anybody know what designation type seu is? Is it the same as use?
SER as Pete pointed out is R for round.Originally posted by allenwayne:
Correct me if I am wrong but isn`t SE 2 hots with a braided grounding conductor and SER has 2 hots 1 grounded conductor and a seperate grounding conductor(uninsulated)