C czars Czars Location West Melbourne, FL Occupation Florida Certified Electrical Contractor Mar 6, 2021 #1 Is something like 4/0,4/0, 4/0, 2/0 SER, with it's outer sheath, considered as one conductor or as over two wires when sizing PVC conduit?
Is something like 4/0,4/0, 4/0, 2/0 SER, with it's outer sheath, considered as one conductor or as over two wires when sizing PVC conduit?
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Mar 6, 2021 #2 czars said: Is something like 4/0,4/0, 4/0, 2/0 SER, with it's outer sheath, considered as one conductor or as over two wires when sizing PVC conduit? Click to expand... A cable assembly is treated as a single conductor in conduit. Watch for oval/flat cables like UF; they're treated as round conductors of the larger dimension.
czars said: Is something like 4/0,4/0, 4/0, 2/0 SER, with it's outer sheath, considered as one conductor or as over two wires when sizing PVC conduit? Click to expand... A cable assembly is treated as a single conductor in conduit. Watch for oval/flat cables like UF; they're treated as round conductors of the larger dimension.