moab88
Member
- Location
- West Virginia
- Occupation
- Journeyman Electrician
I'm upgrading a 200 Amp service. From the Weather Head down to the dual meter base I'm running either 400 or 350 kcmill conductors that will parallel to two 200 A meters. Out of those meters I have a disconnect on each side and from those disconnects I'm going to the panel. NEC states I only need 2/0 for my 2 hots and Neutral (Table 310.12). Table 250.66 states that my GEC coming from the disconnects and going into my panel only needs to be #4 AWG. Why when I look up SER cables they list them as 2/0, 2/0, 2/0, #1?