I have a meter center feeding multifamily units with a 125A breaker with 2/0 AL SER cable. The corridors and units get blown in insulation above ceiling full to deck. 338.10(B)4a says where installed in thermal insulation the cable ampacity must comply with the 60 degree column of 310.15(B)(16) table, which would increase size of feeder to 3/0. would it be correct to say this does not apply because its the main feeder from meter to unit panel and based on the informational note 2 referring to 310.15(B)(7)2 the feeder conductor shall be permitted to have an ampacity not less than 83%? followed by 310.15(B)(7)3 In no case shall feeder for individual dwelling unit be required to be greater than that specified in 310.15(B)(7)(1)or(2).