The job is a residential service change for a 120/240 Volt 200 AMP Service. Due to having to relocate the Panel, I'll need to install a 200 AMP meter with a 200 amp main breaker. As a result, I'll be using a copper (Customer wants copper) SER to feed the 200 amp MLO panel.
I'm aware of 310.15(B)(7) for 120/240 Volt services - 200 AMP @ 83% = 166 Amps
My question is the SER located within thermal insulation, where most of it will be located in the insulation.
I believe that article 338.10 (B)(4) states that when SER cable is located within thermal insulation that it should be sized within the 60 degree column of table 310.15(B)(16).
If that's the case, should I be using 4/O CU SER?