I typically see SER with bare ground. In photo below the ground is insulated. Since this place was built in the ’70’s I’m just curious if there was NM available in #2 AL and or a distinction between SER back then - and if it even matters for the 83% rule, formerly 310.15(b), for a feeder from a meter-main.
I.e. if this were #2 AL NM (not listed as SER) would I still be allowed to protect it with a 100a breaker at meter-main or is it just a stepchild at 60C ? *(can't see any markings on jacket with what is visible at either end).

I.e. if this were #2 AL NM (not listed as SER) would I still be allowed to protect it with a 100a breaker at meter-main or is it just a stepchild at 60C ? *(can't see any markings on jacket with what is visible at either end).