In most diagrams of airfield lighting using constant current (series circuit) it show the wiring in a loop where the outgoing and return cables are in separate conduits. Is this not causing problem due to inductance? I saw an incident in a 208V safety switch in which the electrician passed the conductors in separate knockouts and the switch vibrated. We will be installing new edge lights in a taxiway and planning to run (loop) a single wire around the taxiway and would like to avoid any problem on the system.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
One mitigating factor is that the current is lower than it would be for a parallel circuit.
The effect of inductive reactance will be less important with the high voltage of the series circuit and the magnetic effects of an unbalanced current passing through a ferromagnetic plate will be small for the range of current used in these circuits.
What was the current in the safetty switch where you noticed the vibration?
 