M mstrlucky74 Senior Member Location NJ Nov 1, 2016 #1 So I suggested this panel VE to engineer and he's willing to accept. Going to my panel vendor for deduct. Would this affect the feeders or branch to/from panels? Thanks
So I suggested this panel VE to engineer and he's willing to accept. Going to my panel vendor for deduct. Would this affect the feeders or branch to/from panels? Thanks
ron Senior Member Location New York, 40.7514,-73.9925 Nov 2, 2016 #2 Feeders stay the same. Only breaker AIC ratings change. Trip values are unchanged.