series rated breakers

Status
Not open for further replies.
has anyone seen the errata to the 2005 yet? i usually go to the nfpa site on a regular basis. when the errata comes out i make some copies and hand them out at the office and at school. the way i read the errat is that we have to delete all of 240.93. just wondering why.
 
Re: series rated breakers

I don't feel the section is really needed considering the exact same requirements are one page back in 240.86. :confused:
 
Re: series rated breakers

Bryan, that is exactly right. The provisions in the previous sections apply to the part on supervised industrial installations unless they are changed in that part. :D
 