I understand how series rated breakers are applied (tested and listed combinations) but I never quite had a full understanding of what the rating was based on.
My understanding has always been the upstream breaker in the series rating somehow "current limited" the fault current so that the downstream breaker would see a reduced let-through current which was below its interrupting rating.
For example if the downstream breaker (Breaker B) has a 35kA interrupting rating but a 65kA series rating with upstream breaker (Breaker A) then does Breaker A somehow current limit fault current on the load side of Breaker to below 35kA? So any fault current passing through Breaker A (up to its 65kA rating) will be current limited to Breaker B and thus Breaker B can take on the 65kA rating of the upstream breaker?
So the upstream breaker acts somewhat like a current limiting breaker/fuse?
My understanding has always been the upstream breaker in the series rating somehow "current limited" the fault current so that the downstream breaker would see a reduced let-through current which was below its interrupting rating.
For example if the downstream breaker (Breaker B) has a 35kA interrupting rating but a 65kA series rating with upstream breaker (Breaker A) then does Breaker A somehow current limit fault current on the load side of Breaker to below 35kA? So any fault current passing through Breaker A (up to its 65kA rating) will be current limited to Breaker B and thus Breaker B can take on the 65kA rating of the upstream breaker?
So the upstream breaker acts somewhat like a current limiting breaker/fuse?