Hi all,
I have a few questions regarding series rated combinations:
1) Let's say, for example, the line side device is a fused switch, and it feeds a downstream panelboard with breakers. In order to achieve a series rated combination, must the line side fuse be current limiting? (on a side note, from what i read, i understand that one cannot use the UP-OVER-DOWN method on the line side device (from a current limiting curve) to determine if a combination is series rated due to the dynamic impedance of the downstream breakers... we would be in violation of NEC section 240.86(A) since the downstream breaker would not remain 'passive' during the operation of the line side device. The manufacturer would perform its own in-house testing).
2) In a series rated combination, where the downstream breakers have a lower AIC rating, can the panelboard itself also have a lower SCCR rating to match the breakers? I would assume yes since the upstream line side device is current limiting. and in the case of the panelboard, there would be no issue with dynamic impedance since we're only dealing with the bus bars of the panel.
Thanks in advance!
I have a few questions regarding series rated combinations:
1) Let's say, for example, the line side device is a fused switch, and it feeds a downstream panelboard with breakers. In order to achieve a series rated combination, must the line side fuse be current limiting? (on a side note, from what i read, i understand that one cannot use the UP-OVER-DOWN method on the line side device (from a current limiting curve) to determine if a combination is series rated due to the dynamic impedance of the downstream breakers... we would be in violation of NEC section 240.86(A) since the downstream breaker would not remain 'passive' during the operation of the line side device. The manufacturer would perform its own in-house testing).
2) In a series rated combination, where the downstream breakers have a lower AIC rating, can the panelboard itself also have a lower SCCR rating to match the breakers? I would assume yes since the upstream line side device is current limiting. and in the case of the panelboard, there would be no issue with dynamic impedance since we're only dealing with the bus bars of the panel.
Thanks in advance!