Helping a friend out with a question he sent my way.
We have a 600A panel with a main rated for 50 kAIC. The fault current per the calculations at the main breaker is 30 kAIC therefore the 50 is sufficient. The electricians submitted on a main rated for 50 kAIC but the circuit breakers are only rated for 22 kAIC and they are claiming this is acceptable because they are series rated. I dont really know of anything in between the main and the circuit breakers that would substantially reduce the fault current down to less then 22 kAIC if we have 30 kAIC at the main. Any ideas on this?
PS. I havent really came across any main breaker rated for 50 kAIC but for purposes of discussion I will just assume this is made.
We have a 600A panel with a main rated for 50 kAIC. The fault current per the calculations at the main breaker is 30 kAIC therefore the 50 is sufficient. The electricians submitted on a main rated for 50 kAIC but the circuit breakers are only rated for 22 kAIC and they are claiming this is acceptable because they are series rated. I dont really know of anything in between the main and the circuit breakers that would substantially reduce the fault current down to less then 22 kAIC if we have 30 kAIC at the main. Any ideas on this?