I am confused about this section of the code. How do I "prove" That my downstream circuit breakers that are part of the series combination remain passive during the interruption period of the line side fully rated current limiting device? Is this done through fault current calculations? I've never been asked to prove this before. I am assuming I must submit my details from siemens on the breakers I'm installing. Plus submit Fault current calculations. They are also requiring I make placards stating the Catalog numbers of all breakers. My system is as follows:
Utility stated AIC= 42,000
Single phase system 400A 120/240V EMT 2" 4/0 Parallel conductors (3) per pipe 28' length. terminates to 400A 85KAIC Siemens 3VA53 Molded case breaker.
Downstream to power mod 16 units + 1 house panel. 60A 65 KAIC 2 pole breakers at meters. Siemens Q260HH
To the units shortest distance is 40' longest 175'. Main lug panels the breakers there are 10,000AIC. EMT flex combination.
Thanks in advance
Jason
Utility stated AIC= 42,000
Single phase system 400A 120/240V EMT 2" 4/0 Parallel conductors (3) per pipe 28' length. terminates to 400A 85KAIC Siemens 3VA53 Molded case breaker.
Downstream to power mod 16 units + 1 house panel. 60A 65 KAIC 2 pole breakers at meters. Siemens Q260HH
To the units shortest distance is 40' longest 175'. Main lug panels the breakers there are 10,000AIC. EMT flex combination.