R raven Member Oct 17, 2019 #1 If a panel is series rated, and the rating is 22k, can a breaker be installed in the panel higher than this rating?
ron Senior Member Location New York, 40.7514,-73.9925 Oct 18, 2019 #3 Yes, either for the full SCCR or also series rated with the upstream for the available fault current
J Julio Cesar Member Location Mexico Oct 18, 2019 #4 raven said: If a panel is series rated, and the rating is 22k, can a breaker be installed in the panel higher than this rating? Click to expand... yes you can rate up, but not low.