Series Rated System

Status
Not open for further replies.

timm333

Senior Member
Location
Minneapolis, MN
Occupation
Electrical Design Engineer
Is Exhibit 240.14 of NEC handbook correct? Motor full load current (FLA) is 100A and the interrupting of load breaker is 10 kA. FLA is equal to 1% of interrupting so it does not exceed 1%. But the note below the exhibit says that it exceeds 1%. Thanks.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
That figure in the 2014 handbook (the only one I have) says motor full load current is greater than 100 amps.
 