My Cutler Hammer CH series 200A panelboard has a 35kaic main and the new 3rd gen AFCI cbs have a "standard" 10kaic rating.
Does the 35kAIC main protect the 10kAIC cbs under it? Is it current limiting?
The lesser quality BR series distribution breakers have a 22kAIC rating.
I'm going to call the factory tomorrow but I don't see why the lesser BR cbs have a higher rating.
I'm not worried about it because this a pole mounted xfmr over 100 feet away.
We also have surge protector in the panel.
any ideas?
Cat #: CH42BPN200K
200 AMP, 120/240V AC, 1-Phase, Main Breaker Loadcenter, 35 kAIC, 42-Space, 42-Pole, Copper Bus, NEMA 1 - Indoor.
Cat #: CHSPT2ULTRA
Surge Protection Device, 4-Mode, Type 2, 1-Phase, 120/240V AC, 2-Pole, 3-Wire, Max Surge Current Per Phase: 108 kA, NEMA 4, Panel Mount.
Cat #: CHCAF120PN
20 Amp, 1-Pole, Type CH Combination Fireguard/Arc Fault Circuit Interrupter with Plug-On Neutral, Common Trip, 10 kAIC, 120/240 VAC.
Does the 35kAIC main protect the 10kAIC cbs under it? Is it current limiting?
The lesser quality BR series distribution breakers have a 22kAIC rating.
I'm going to call the factory tomorrow but I don't see why the lesser BR cbs have a higher rating.
I'm not worried about it because this a pole mounted xfmr over 100 feet away.
We also have surge protector in the panel.
any ideas?
Cat #: CH42BPN200K
200 AMP, 120/240V AC, 1-Phase, Main Breaker Loadcenter, 35 kAIC, 42-Space, 42-Pole, Copper Bus, NEMA 1 - Indoor.
Cat #: CHSPT2ULTRA
Surge Protection Device, 4-Mode, Type 2, 1-Phase, 120/240V AC, 2-Pole, 3-Wire, Max Surge Current Per Phase: 108 kA, NEMA 4, Panel Mount.
Cat #: CHCAF120PN
20 Amp, 1-Pole, Type CH Combination Fireguard/Arc Fault Circuit Interrupter with Plug-On Neutral, Common Trip, 10 kAIC, 120/240 VAC.