SERIES RATING CHART
Toros
Tujunga, CA
HI
Would you check the series rating chart and notes I prepared to paste on plans for department approvals.
thank you
see attached
  • Series Rating-2014.pdf
HI
thank you
see attached
Multiple typos. A missing word. Spelling error.
What is the purpose of this note? It does not seem to add all that much. Boilerplate rarely does. Maybe clean it up and put it in the specs and just reference it as a note.
HI
thank you
see attached
Reword to get rid of parentheses.
Instead of stars *, use numbers
There is no such thing as motors', they are simply motors
Do not use periods in abbreviations unless needed or clarity such as the word "NO" versus normally open N.O.; especially don't use them in the same abbreviation and then not, i.e. OCPD vs. O.C.P.D.
3rd paragraph; the fault current is applicable regardless of who provides the information. Suggest removing reference to local utility company.
There is no such thing as an "Equal" part or product. Suggest using term "Approved Alternate" Who is approving it anyway?