ajb5102
Member
- Location
- Pittsburgh, PA
- Occupation
- Mechanical Engineer
When series rating testing, a main breaker (65 kAIC) upstream from a branch breaker (10kAIC), the circuit is calibrated for the 65k AFC prior to the test beginning. After set-up, and when the fault is initiated, will the branch breaker interrupt all 65kA; or is the AFC (at the moment of interrupt, at the location of the branch) reduced dramatically by the impedance of the breakers and conductors (from the power supply to the main, and from the main to the branch, and back to the power supply)?