I am not able to share a one line since it's classified.
Interesting. Pen and paper sketch showing interconnection of generic CBs is "classified" - but describing with words is not.
Okay. (Just teasing, not slapping)
I'd love to rip out the HD, replace it by a HJ and call it a day.
You want to replace the gen CB with a higher rated CB, same on as is used for the panel normal feeder?
In NORMAL, feed is a valid series rating. Nothing wrong here. ATS does not matter.
In EMERGENCY, feed is gen to HD (18KA) to Panel EHB (AIC rating unknown) Couple of questions:
What is the AIC rating for the EHB panel CBs?
What is the available short circuit current of the generator?
Following is pure conjecture on my part:
The gen CB is likely sized for 1.25 x genFLA. Say 80A. I don't know if the gen is 208V, 480V, 3phase, 1phase. Figuring 480V, 3ph, that is a 50KW (65KVA) generator.
Generators are notoriously light on ASCC. Sub transient reactance Xd" maybe .20 to .25. I would expect the gen short circuit current to be ~ 80/.2 = 400A. Yep, that low.
So, running on the gen, the question is not, "Can the EHB CB interrupt the Max SCC?"
Rather, "How long will it take the EHB to open with only 400A SCC?"
With the information we have the install appears fine.