jim dungar said:
There are very very very few series ratings that involve three breakers in series. I have never heard of 4 breakers in series.
Jim,
this is very similar to my topic "3-level series rating"
And believe me, there will come up more and more of this topics.
I see the reason in the new UL508A - Marking of the SCCR value.
Why - because up to now every one did it by some sort of calculation, i.e. looking of the let through of the upstream device and compare this let through with the capability of the downstream device. If the let through of the upstream device is not higher than the capability of the downstream we would call it okay.
We are also aware that this may not be a well coordinated system in terms of selectivity.
But it is the way as many of the IEC Maschine building companies are working
In the IEC we even do also have specific breaker data, which is called I((sub))cm, this is a peak value specified by the manufacturer of the breaker, able to be compared with the peak let through of upstream devices.
It is called "making capacity" and tells us at which level of peak value the contacts are starting to drive apart.
AND NOW:
UL508A trells us that we have to have an SCCR value but gives us only limited chances to get to higher values.
Gustav