TALO
Member
- Location
- Portland, Oregon, USA
Hello all,
I have a couple questions on the series rated equipment...
If we have a transformer feeding a building with an available fault current of 18,000 amps and wanted to go with a series-rated system rather than fully-rated, is it acceptable to use a disconnect with fuses rated at 200kAIC feeding a main breaker rated at 25kAIC, where the rest of the breakers in the panel are only rated 14kAIC?
The way I understand it, the panel guts would also need to be rated above the available 18k (so as not to explode before hitting the main breaker), but I'm having some difficulties finding this rating on any guts.
Another note, the fuses (rated at 200kAIC) have a peak let through current of 9k amps, so would this mean I don't have to worry about the rating on my panel (assuming it can withstand at least the 14k my branch circuit breakers are rated for)?
Lastly, the NEC says that a series rated system must either be engineered, or the equipment tested and marked for such use. Would this be a testing facility that I literally send my equipment in to be tested, or are the kAIC ratings on the fuses/breakers sufficient?
Thanks in advance for your responses!
I have a couple questions on the series rated equipment...
If we have a transformer feeding a building with an available fault current of 18,000 amps and wanted to go with a series-rated system rather than fully-rated, is it acceptable to use a disconnect with fuses rated at 200kAIC feeding a main breaker rated at 25kAIC, where the rest of the breakers in the panel are only rated 14kAIC?
The way I understand it, the panel guts would also need to be rated above the available 18k (so as not to explode before hitting the main breaker), but I'm having some difficulties finding this rating on any guts.
Another note, the fuses (rated at 200kAIC) have a peak let through current of 9k amps, so would this mean I don't have to worry about the rating on my panel (assuming it can withstand at least the 14k my branch circuit breakers are rated for)?
Lastly, the NEC says that a series rated system must either be engineered, or the equipment tested and marked for such use. Would this be a testing facility that I literally send my equipment in to be tested, or are the kAIC ratings on the fuses/breakers sufficient?
Thanks in advance for your responses!