hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I understand I had some version of this previously but was little confused about previous situation.
Please see attached sketch region label #1 is series rated with bkr #1 and bkr #2. Region label # 2 is series rated with bkr #2 and bkr#4.
Region label #3 is series rated with bkr #4 and bkr#7.
Assume motors full load exceed 1%.
Following questions:
1. I am guessing but not sure but regions label #1,#2,#3 should not be series rated because of NEC 2014 section 240.86(C). If not then which regions should not be series rated NEC 2014 section 240.86(C)?
2. Fault current of motors can travel anywhere there is fault. If fault is between region #1 I am not sure how it would work. Utility fault current would go downstream and motor fault current go upstream and thus cancel some of the utility fault currents or not? If allowed to be series rated Region #1 then what is logic behind it
3. If fault in between Region #3 then motor faults current and utility fault current would add so line side of panelboard breaker would see motor fault currents as well as utility. If Region is allowed to have series rating and not fully rated 240.86(C) then would not the panelboard breaker be melted given it is less than available fault current? Yet if allowed to be series rated then what is logic behind that allowance?
Please see attached sketch region label #1 is series rated with bkr #1 and bkr #2. Region label # 2 is series rated with bkr #2 and bkr#4.
Region label #3 is series rated with bkr #4 and bkr#7.
Assume motors full load exceed 1%.
Following questions:
1. I am guessing but not sure but regions label #1,#2,#3 should not be series rated because of NEC 2014 section 240.86(C). If not then which regions should not be series rated NEC 2014 section 240.86(C)?
2. Fault current of motors can travel anywhere there is fault. If fault is between region #1 I am not sure how it would work. Utility fault current would go downstream and motor fault current go upstream and thus cancel some of the utility fault currents or not? If allowed to be series rated Region #1 then what is logic behind it
3. If fault in between Region #3 then motor faults current and utility fault current would add so line side of panelboard breaker would see motor fault currents as well as utility. If Region is allowed to have series rating and not fully rated 240.86(C) then would not the panelboard breaker be melted given it is less than available fault current? Yet if allowed to be series rated then what is logic behind that allowance?