wireman1 Senior Member Mar 18, 2017 #1 can you run 4 wire sers feeder cable al in a commercial bldg. apts do any other I codes require this I cant find this anywhere in the nec
can you run 4 wire sers feeder cable al in a commercial bldg. apts do any other I codes require this I cant find this anywhere in the nec
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Mar 18, 2017 #2 It depends on how the building is typed. Is it type I, II, III, IV or V
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Mar 18, 2017 #3 Also it cannot be use above drop ceilings in other than one or two family dwellings.
H Hendrix Senior Member Location New England Mar 20, 2017 #4 infinity said: Also it cannot be use above drop ceilings in other than one or two family dwellings. Click to expand... That may be changing in NH. It already has in MA,VT, and ME
infinity said: Also it cannot be use above drop ceilings in other than one or two family dwellings. Click to expand... That may be changing in NH. It already has in MA,VT, and ME