• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Service 400A

Leonan

Member
Location
Massachusetts
Occupation
Electrician
Hello everyone, I have a question at work. To provide a 400A service for 6 units, I will use only one pipe and leave the wires in parallel. So will I have to apply table 310.25 C1? Which would be 400A/80%: 500A/2: 250A per phase. Would it have to be a 350 kmil aluminum parallel?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Are you asking about the derating or ampacity adjustment table? Youve got a misprint that's T310.15(C)(1). If so your calculations are correct.
 