Hello everyone, I have a question at work. To provide a 400A service for 6 units, I will use only one pipe and leave the wires in parallel. So will I have to apply table 310.25 C1? Which would be 400A/80%: 500A/2: 250A per phase. Would it have to be a 350 kmil aluminum parallel?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Are you asking about the derating or ampacity adjustment table? Youve got a misprint that's T310.15(C)(1). If so your calculations are correct.
 